[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[BLDG-SIM] Hornet's Nest - Thermal Balance Calculations



I agree with both Dan Nall's and Bruce Spurlock's comments regarding detailed thermal balance loads calculations vs. the real needs of the energy simulation community, and would like to comment further as to how an HVAC system actually responds to building loads.

First, let me comment on my qualifications and biases.  In the late '70s, I was one of the original DOE-2 authors, responsible for many of the PLANT algorithms.  After leaving LBNL in the early '80s, I designed HVAC systems and controls for over a decade.  Since the early '90s I have worked closely with JJH&Associates (Jeff Hirsch), and wrote or co-wrote much of the new code in the air-side and water-side portions of DOE-2.2.  With JJH, I am currently the lead author of a component-based refrigeration/mechanical system module slated for the next major DOE-2 release.

In a nutshell, an HVAC system responds to a building's thermal loads via a thermostat that senses the deviation of zone temperature from setpoint.  Given this, a highly relevant question is, "How accurately does a thermostat measure space temperature, and how seriously can the error in measurement affect the heat extraction rate of the HVAC system?"

In terms of accuracy, there are a number of factors that preclude temperature measurements more accurate than 2-4°F, including:

  1. Thermostat location - Energy simulation programs assume the thermostat measures the air temperature, with a possible modification for radiant flux.  In reality, a thermostat measures a combination of air temperature, radiant temperature, and wall temperature.  The interplay between these factors can be significant.  For example, most residential thermostats incorporate a small internal resistance heater that energizes whenever the space heater is operating.  Otherwise, the lag in sensed vs. actual space temperature will result in excessive temperature overshoot and discomfort. (Many thermostats allow you to adjust this "anticipator".  If your heater runs for long periods of time and overshoots the setpoint, you need to reduce the anticipator's resistance, thereby increasing the electric current and internal heating rate.  If your heater short cycles, you need to increase the resistance, thereby reducing the current and heating rate.)
  2. Temperature stratification/gradients - Temperature gradients typically exist between outer surfaces and inner surfaces, and between the floor and ceiling.  A VAV system in the heating mode can easily have a vertical gradient of 10-20°F due to air stratification.  (How many thermal balance calculations recognize that VAV systems produce a hot ceiling surface during heating, and a cold surface during cooling??)  In the cooling mode, an HVAC system typically has a gradient of 20-30°F between supply and return air.  The supply air does not instantaneously mix with room air; instead it flows along the ceiling and down the walls as it gradually mixes.  A thermostat located in this partially-mixed regime may read a temperature significantly different than the average room temperature.  Worse, the error is not constant, it varies as the supply air volume and temperature varies.  A CFD program could take these effects into account, but would require the location of the thermostat to be explicitly identified, as well as the shape and location of all furniture, as well as the location and performance characteristics of all supply diffusers and return registers.  And of course, you would have to specify which interior doors are open and which are closed!  This level of detail is hardly practical in most cases.
  3. Calibration - Electronic thermostats are significantly more accurate than the old pneumatic ones, but may still be in error by 0.5-1.5°F.
  4. Thermostat wars - He's hot, she's cold.  Ask any auditor how many thermostats they find with broken "tamper proof" covers.  Since the goal of any HVAC system design is comfortable, productive people, it makes sense that people be allowed to adjust their space temperature to match their mood or their physiological needs.  But that creates one more unknown in the simulation model.
So, if a thermostat may be off by 2-4°F from what you, the building simulator, thinks is the setpoint, what error does this cause in the simulation?  The intent of a thermal balance calculation is to be able to calculate the instantaneous temperature at any given time so that the instantaneous HVAC load can be calculated.  But, if a thermostat is off by 2°F and has a throttling range of 4°F, then the error in the HVAC system's instantaneous extraction rate may be 50%!!

What this means is that it is impossible to determine the instantaneous load at any given point in time.  A simulation program really cannot determine whether a building peaks at 3:30 p.m. or 4:00.  The most you can expect is that a program should be able to place the loads on the HVAC system within an hour or so of when they actually occur.  Numerous studies have demonstrated that both thermal balance and weighting factor solutions have this resolution.  I am not aware of any study that has demonstrated any real-world difference in accuracy between the two methods.  Even if the physical parameters could be exactly specified and calculated, the error in the human factors could not.

For these reasons, as well as the concerns enumerated by Dan and Bruce, JJH and consultants have chosen to focus primarily on improved mechanical system algorithms and user interfaces. We believe that improvement in these areas are of the greatest value to the user community.
 
 
 
 

begin:          vcard
fn:             Steven D. Gates
n:              ;Steven D. Gates
adr;dom:        11608 Sandy Bar Ct.;;;Gold River;CA;95670-7645;
email;internet: steve-gates@xxxxxxxxxxx
tel;work:       (916) 638-7540
x-mozilla-cpt:  ;0
x-mozilla-html: FALSE
version:        2.1
end:            vcard



======================================================