In an earlier posting Steven Gates wisely urged us to account for steam and HW loop losses and wrote:
Hot-water loops can also have very large losses; I have found that the losses in VAV/hot-water reheat systems typically exceed the annual reheat load.
I'm curious if this is by measurement or simulation? Are "the losses" just the piping heat losses, or does that include boiler losses and valve leakage? I presume this observation applies (as a "typical" finding) mostly to California and other moderate climates. Does anyone else see evidence of this as a "typical" situation?

Recently I've had the opportunity to compare actual heating, and reheat loads with simulated loads for both HW and resistance heating systems. Perhaps I got a little sloppy in some of my simulation assumptions, but in every case, measured heating loads were greater than simulated (including resistance reheat systems without loop losses). In one case, of incredibly poor new building envelope detailing and optimistic simulated building characteristics, the measured heating use was 5-10x the simulated values. Because I've seen this under-prediction in data from electric reheat, I've mostly assumed the simulation problems were in the zone characteristics, but the quote above makes me wonder if I also need to pay more attention to the loop and boiler. In most of these comparisons, the real cooling energy was close to the simulated cooling energy or slightly over-predicted.

Many assumptions about particular components, arrangements, and control schemes can cause under-prediction of both reheat needs and loop losses, while having smaller or negative effects on cooling energy.
Pardon the somewhat non-parallel structure. For the most part, the actual/real situation is described first.

Including:
Envelope
Walls that "the wind blows through," in reality, but not in the model
Even in better buildings, the ASHRAE 90.1 model assumption of zero occupied-period infiltration is not a valid assumption for real building pressures, and characteristics (lobby traffic, non-curtainwall construction, wind over 10 mph, .... ). This is just for comparison purposes.
Walls with lots of funky exposed steel penetrations, headers, columns that somehow didn't get averaged into the already miserable modeled steel stud wall R-values.
Real above grade slab edges without any functional insulation that were modeled as underground, or insulated, or both, or ignored.
Real blinds are often deployed for glare control, reducing solar gains that offset modeled heating loads, and may not be modeled in "90.1" models
Models often leave out shading from other buildings, terrain, and landscaping.
In DOE2, the simple shading coefficient method over-predicts actual solar heat gains in high-incidence angle (winter E&W) situations.
Because of the proportionally higher losses from the greater surfaces, corner zones may have a substantially higher balance point temp (so the heat is on below a higher ambient) than "thermal blocks" modeled with one exposure's glazing only. This may significantly increase raw heating loads, and will increase loop losses from a lengthened boiler and HW loop operating season.

Internal Loads
Actual W/sf plug loads are not the same over the building, though they may get modeled that way for simplicity. Many of the larger plug loads (printers, copiers, servers, pantries...) tend to be clustered in core areas.
Actual building occupancy and associated heat gain is usually much lower than the design occupancy.
Even in non-"daylighting" real buildings, lights and their heat gains, may be off in a significant # of perimeter zones, though a model has a schedule of 90% on all day.

Zone control
Winter supply air temps cooler than assumed.
Overall supply air temps cooler than assumed to satisfy one zone that is starved for air, or overloaded with electronics.
Minimum perimeter primary airflows higher than assumed or specified.
Thermostats installed on exterior walls.

Plant & Loop losses
No reset of HW loop temps, even during very mild weather, contrary to assumption.
Giant atmospheric boilers with constant primary HW flow, operating at 2% load to serve one or two zones for reheat. (DOE2 users need to be careful, because modeled boiler efficiency is held constant below the cycling limit, in reality it can get much worse.)
HW loops operating at such high differential pressures that leakage through heating coils is almost assured. This can't even be modeled in DOE2.
Real piping losses obviously greater than those modeled with adherence to the ASHRAE 90.1 ECB method instruction that "Piping losses shall not be modeled in either building model." In the ASHRAE methodology, if the proposed building has HW heat, then the budget building also does. However, these assumptions can get carried over into overall building energy cost projections and comparisons, when one is in a hurry, or does not want to explain to the clients why their real building is projected to use more energy than the "minimally-compliant code" building.

These are often characteristics that cannot be directly transferred from plans to simulation inputs. Some are things that can't be known in advance, at least not with precision. Many can and should be fixed after the fact, or avoided with proper detailing and specification. Some just require a little careful modeling thought. 
-- 