[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[BLDG-SIM] "Cool Roofing"



Hello:
 
Here's my $0.05 worth.
 
First, FSEC, LBNL and others have done lots and lots of work on this...and the "results" are very dependent on what is going on
below the roof. For example, if there are ducts, what model is used, etc. Information about what they have
done can be found in papers by Parker, and Fairey, etc.
 
Second, to be correct, one needs a simulation model that has radiation and natural convection calculated
correctly in the attic -- usually outside the domain of DOE-2, or powerDOE, for example see the work by
Mario Medina et al. at the University of Kansas.
 
Third, if one insists on using DOE-2 we have found that it makes a big difference when one turns on the
CUSTOM-WEIGHTING-FACTORS by setting the floor weight equal to zero.  This, of course needs
lots of other things, like a different floor model, and real materials, etc., not for the faint-of-heart.
 
Finally, I have my doubts about DOE-2's radiative coupling to the sky, its "rain" simulation, and its "dewpoint" assumptions,
based on some simulations that we have made where we compared the data from measured attic temperatures from a Habitat House that
showed the simulation losing more heat than the real attic did -- interesting stuff that will be presented in a paper someday, report
available from the ESL soon.
 
Here's an annotated bibliography that we recently prepared for the California Energy Commission on the topic.  
 
Jeff
 
Akbari, H. (1998). Cool Roofs Save Energy. ASHRAE Transactions, Vol.104, Pt. 1B, pp. 783-788.

 

This paper discusses about field data documenting the effect of white roofs that has been found to reduce the air conditioning load in individual buildings in California and Florida by between 10% and 50%, depending on the thickness of insulation beneath the roof. In addition 'cool' roofs can limit or reverse the urban heat island effect and can reduce low-level ozone concentrations. The paper also presents simulated savings for several U.S. metropolitan areas and briefly discusses policy and implementation issues such as ratings and ASHRAE standards.

 

Akbari, H., Gartland, L. M., & Konopacki, S. J. (1998). Measured Energy Savings of Light-colored Roofs: Results from Three California Demonstration Sites. ACEEE 1998 Summer Study on Energy Efficiency in Buildings: Efficiency & Sustainability, Vol. 3, pp. 3.1-3.12.

 

This study demonstrated the impact of roof albedo in reducing cooling energy use in three commercial buildings in California. Increasing the roof reflectance from about 20% to 60% dropped the roof temperature on hot summer afternoon by about 45°F. Savings are a function of both climate and the amount of roof insulation. The cooling energy savings for reflective roofs are highest in hot climates. A reflective roof may also lead to higher heating energy use. Reflective coatings are also used in commercial building to protect the roofing membrane. Reflectivity of coatings changes with weathering and aging which have an effect on building cooling-energy savings. 

 

Akbari, H, & Konopacki, S. J. (1998). The Impact of Reflectivity and Emissivity of Roofs on Building Cooling and Heating Energy Use. Proceedings of the ASHRAE/DOE Conference on Thermal Performance of the Exterior Envelopes of Buildings VII, Clearwater Beach, FL., pp. 29-39.

 

This paper summarizes the result of computer simulations and analyses the impact of roof albedo and emissivity on heating and cooling energy use. The simulations are performed for eleven representative climates throughout the country. Several residential and commercial prototypical buildings are considered for these simulations. In hot climates, changing the roof emissivity from 0.9 (emissivity of most nonmetallic surfaces) to 0.25 (emissivity of fresh and shiny metallic surfaces) can result in a net 10% increase in annual utility bills. In colder climates, the heating energy savings approximately cancel out the cooling energy penalties from decreasing the roof emissivity. In very cold climates with no summertime cooling, the heating energy savings resulting from decreasing the roof emissivity can be up to 3%.

 

Akbari, H., Konopacki, S. J., Eley, C. N., Wilcox, B. A., Van Geem, M. G. & Parker, D. S. (1998). Calculations for Reflective Roofs in Support of Standard 90.1. ASHRAE Transactions, Vol. 104, Pt. 1B, pp. 976-987.

This paper summarizes the results of a simulation effort in support of ASHRAE SSPC 90.1 for the inclusion of reflective roofs in the proposed standard. Simulation results include the annual electricity and fuel use for two building types, residential and non-residential. The 90.1 Envelope Subcommittee DOE-2 prototype building and operating schedules were used. The parametric simulations were performed for 19 climate bins, as defined in the current 90.1 draft; a range of roof absorptivities from 0.25 to 0.95; and three roof U-factors (corresponding to roof insulation of R3, R11, and R38). The results are condensed into climate-dependent adjustment factors to reduce roof insulation for buildings with reflective roofs such that the net energy use of the building stays constant when compared with the energy use of a dark-colored roof.

 

Akbari, H., Konopacki, S. J.,  & Parker, D. S. (2000). Updates on Revision to ASHRAE  Standard 90.2: Including Roof Reflectivity for Residential Buildings. ACEEE 2000 Summer Study on Energy Efficiency in Buildings: Efficiency & Sustainability, Vol. 1, pp. 1.1-1.11.

 

This paper discusses the results of a simulation effort in support of ASHRAE SSPC 90.2 for inclusion of reflective roofs in the proposed standard. Simulation results include the annual electricity and fuel use for a prototypical single-family one-story house. The 90.2 Envelope Subcommittee DOE-2 prototype building and operating schedules were used. The parametric simulations were performed for the following scenarios and combinations thereof: 3 heating systems, 4 duct and duct insulation configurations, 5 levels of roof reflectivity, and 4 levels of attic air change rate. The simulations were performed for 32 climate regions. The results are condensed into climate-dependent adjustment factors that equivalent reductions in roof insulation levels corresponding to increased roof reflectivity. Results indicate that in hot climates, increasing the roof reflectivity from 20% to 60% is worth over half of the roof insulation.

 

Akbari, H., Levinson, R. & Berdahl, P. (1996). ASTM Standards for Measuring Solar Reflectance and Infrared Emittance of Construction Materials and Comparing their Steady-State Surface Temperatures. ACEEE 1996 Summer Study on Energy Efficiency in Buildings: Efficiency & Sustainability, Vol. 1, pp. 1.1-1.9.

 

This paper describes the technical issues relating to development of two American Society for Testing & Materials (ASTM) standards, E 903 – Test Method for Solar Absorptance, Reflectance, and Transmittance of Materials Using Integrating Spheres, and E 408 – Test Methods for total Normal Emittance of Surface Using Inspection-Meter Techniques. The study addresses the measurement of the solar reflectance of the horizontal surfaces in the field and translating the results into a comparative index. SRI is an excellent predictor of relative surface temperature for materials with high infrared emittance and is generally insensitive to variations in convection coefficients, ambient temperature, and sky temperature.

 

Akbari,H., Taha, H., & Sailor, D. (1992). Measured Savings in Air Conditioning from Shade Trees and White Surfaces. Proceeding of the ACEEE 1992 Summer Study on Energy Efficiency in Buildings: Efficiency & Sustainability, Vol. 9, pp. 9.1-9.10.

This study discusses the measured saving in air-conditioning electricity use which resulted from painting roofs white and planting shade trees for six houses and a school bungalow in Sacramento, CA. Preliminary data indicate the painting roof white of one of the houses eliminated air-conditioning energy use about 12 kWh/day and 2.3 kW in peak power. Painting the roof and one wall of a school bungalow white reduced its air-conditioning energy use by over 50%. Shading the west windows, south windows, and air-conditioning  condenser units of two houses with trees appear to have lowered cooling electricity use by 10 to 40%.

 

Akridge, J. M. (1998). High-albedo Roof Coating - Impact on Energy Consumption. ASHRAE Transactions, Vol. 104, Pt. 1B, pp. 957-962.

 

The paper addresses the recent tests conducted on a 12,000ft² single-story building used as an educational center identified high roof temperatures as a significant problem. The galvanized roof frequently reached temperatures above 180°F. Considerable heat energy reached the non-ventilated attic, resulting in temperatures as high as 105degF during the peak of summer. Although the HVAC units were equipped with insulated return ducts, these temperatures increased energy conduction through the duct insulation and through the ceiling insulation into the conditioned space. The roof was coated on March 28 and 29, 1995, with a high-albedo acrylic coating developed to control thermal gain and rust. Tests show installation of the thermal-control roof coating reduced the peak roof temperature to 120°F and significantly decreased the energy flow through the roof and ceilings. Tests show that the high-reflectivity roof coating reduced HVAC energy consumption in a range from 8.7% to 27.5%, depending on the solar radiation and the ambient temperature.

 

Anderson, R. W. (1989). Radiation Control Coatings: An Underutilized Energy Conservation Technology for Buildings. ASHRAE Transactions, Vol. 95, Pt. 2, pp. 682-685.

 

The paper points out that the application of radiation control coatings (RCCs) to exterior roof and wall surfaces can effectively block solar heat gains and significantly reduce cooling energy consumption and the sizing of cooling equipment in warm climates. The application of RCCs remains underutilized and is not yet recognized in building energy codes. The paper discusses the status of RCC technology and the benefits to be gained from the use of RCCs, including estimated reductions in cooling requirements and energy consumption and suggests projects to demonstrate the full potential of RCCs technology for building applications.
 
Bretz, S. E., & Akbari, H. (1994). Durability of High-Albedo Roof Coatings. ACEEE 1994 Summer Study on Energy Efficiency in Buildings: Efficiency & Sustainability, Vol. 9, pp. 9.65-9.75.

The study addresses the aging characteristics of high-albedo roofs. Twenty-six spot albedo measurements of roofs were made using a calibrated pyranometer. The decrease in albedo depends on the coating itself, the texture of the surface, the slope of the roof and the nearby sources of dirt and debris. The largest decrease in albedo occurs in the first year, at a reduction of about 20%. After the second year, the incremental decrease in albedo can be small, lowering saving estimates by 10-20%. Washing the high-albedo coatings returned the albedo to 90-100% of the estimated original value but it is not cost-effective if only concerned with cooling-energy saving.

 

Carlson, J. D., Christian, J. E., & Smith, T. L. (1992). In Situ Thermal Performance of APP-modified Bitumen Roof Membranes Coated with Reflective Coatings. Proceedings of the ASHRAE/DOE Conference on Thermal Performance of the Exterior Envelopes of Buildings V, Clearwater Beach, FL., pp. 420-428.

 

A multi-faceted field research program regarding seven atactic polypropylene (APP) modified bitumen membrane roof systems and four reflective coatings began in 1991. This long-term project is evaluating the performance of various APP-modified bitumen membranes (both coated and uncoated), the comparative performance of coating application soon after membrane installation versus pre-weathering, coating performance, and aspects of recoating. Reports progress on the in-situ thermal performance of the various types of coated membranes compared to the thermal performance of the exposed membranes. The thermal performance of an adjacent ballasted ethylene propylene diene terpolymer (EPDM) roofing system is also described.

 

Fawcett, S. L., Shull, P.D., & Smith, D. (1992). Application and Experience in the Use of Aluminium Chips as a Reflective Surface for Commercial Roofing. Proceedings of the ASHRAE/DOE Conference on Thermal Performance of the Exterior Envelopes of Buildings V, Clearwater Beach, FL., pp. 417-419.

 

The paper contains the information of using thin aluminium chips as a reflective surface for commercial roofing. Chips can be field or factory applied. Solar reflectivity measurements indicate that approximately 70% of the full solar spectrum is reflected. A brief review of the early roofing projects indicates that retained reflectivity and extended roof life are being achieved. The paper describes characteristics of such roofing surfaces, how the product is applied to roofs, and the experience to date in their application and performance.

 

Fisette, P. (1996). “Roofing and Siding Rehabs Get an Energy Fix”, Home Energy Journal, November-December, pp.25-31.

 

This paper explains the idea of using thin aluminum chips as a reflective surface for commercial roofing. The paper states about reflectivity of the chips (approximately 70%) that more than 96% is still retained over 10 years. Advantages of roof temperature reduction, roof life as well as characteristics of roofing surface, how the product is applied to roofing, and the experience to date in their application and performance are also described.

                                            

Gartland, L. M., Konopacki, S. J., & and Akbari, H. (1996). Modeling the Effects of Reflective Roofing. ACEEE 1996 Summer Study on Energy Efficiency in Buildings: Efficiency & Sustainability, Vol. 4, pp. 4.117-4.124.

 

This paper describes a function that was written to incorporate the attic heat transfer processes into the DOE-2 building energy simulation. This function adds radiative, convective and conductive equations to the energy balance of the roof. Results of the enhanced DOE-2 model were compared to measured data collected from a school bungalow in a Sacramento Municipal Utility District monitoring project. The function improves the accuracy of DOE-2 in modeling the effects of high albedo roofing but still over-predicts the daily energy use of both high and low albedo roofs. The yearly energy savings of a white roof may be as much as four times higher than is currently predicted by DOE-2.

 

Griggs, E. I., & Shipp, P. H. (1988). The Impact of Surface Reflectance on Roofs: An Experimental Study. ASHRAE Transactions, Vol. 94, Pt. 2, pp. 1626-1642.

 

The paper is the study about the thermal effects of black versus white membranes on an insulated low slope roof over an 18 month period. White or black polyisobutylene (PIB) membrane was used. Seasonal distinctions in the measured data between black and white membranes are reported. Included are cumulative and instantaneous heat fluxes and hourly surface temperature variations. Peak membrane temperatures were observed to differ by up to 50 ºF during the day. Nighttime differences in membrane surface temperatures were negligible. Changes due to dirt accumulation and local environmental factors were observed in surface reflectance values calculated from the energy balance at the roof membrane and from reflectometer measurements.

 

Hildebrandt, E. W., Bos, & W., Moore, R. (1998). Assessing the Impact of White Roofs on Building Energy Loads. ASHRAE Transactions, Vol.104, Pt. 1B, pp. 810-818.

 

The study states the impact of white roof coatings on energy loads in three non-residential buildings in Sacramento. Hourly metered loads were designed to isolate the effects of white roof coatings on building cooling loads from changes in cooling loads due to variations in outdoor temperatures. Basic multiple linear regression model used to weather normalize energy consumption data was expanded to include hourly solar radiation or insolation levels as explanatory variables, along with explanatory variables representing outdoor temperatures. Results indicate that the effect of solar insolation levels on cooling energy consumption was significantly decreased after the application of white roofs in all three buildings. Savings estimates based on this approach range from 17% to 39% of total cooling loads, or .35kWh to .68kWh per square foot of treated roof area per year.

 

Kochhar, G. S., Osborne, R. W. A., & Lewis, E. R. (1992). Enhancement of Thermal Performance of Domestic Roofing System for Tropical Climes. Proceedings of the ASHRAE/DOE Conference on Thermal Performance of the Exterior Envelopes of Buildings V, Clearwater Beach, FL., pp. 429-439.

 

This paper studies a series of side-by-side tests using model roof assemblies have been conducted to determine the potential of radiant barriers for enhancing the thermal microclimate of local domestic, single-storey low-cost housing, for tropical climates. A comparative system was adopted, using two identical test models, one an unchanging reference and the other a test unit for examining the behavior of various radiant barrier and ceiling configurations. The paper presents the design details of the outdoor testing system used and the results of comparative testing of aluminium foil and aluminium paint with regard to their effectiveness as radiant barriers. Experimental results showed that the low-cost aluminium paint, although not as effective as aluminium foil, does have an enhancing effect on the thermal performance of the roof assembly system.

 

Konopacki, S., & Parker, D. (1998). “Saving Energy with Reflective Roofs”, Home Energy Journal, November-December, pp. 9-10.

 

This paper contains information of five final case studies out of ten case studies that the Florida Solar Energy Center conducted in Florida during midsummer over a period of four years. The studies measured the effect of increasing the roof surface solar reflectance on air conditioning energy use. The studies did not recommend painting or coating a conventional shingle roof white because it can lead to potential moisture damage. In all locations, reflective roofs reduced space-cooling varying from 13% to 58%. Heating consumption was increased only slightly, from 3% to 6%.    

 

MacDonald, J. M., Courville, G. E., Griggs, E. I., & Sharp, T. R. (1989). A Guide for Estimating Potential Energy Savings from Increased Solar Reflectance of a Low-sloped Roof. Proceedings of the ASHRAE/DOE Conference on Thermal Performance of the Exterior Envelopes of Buildings IV, Orlando, FL., pp. 348-357.

 

This paper describes the methodology and limitations of an easy-to-use guide for calculating energy and cost saving resulting from a change in the solar reflectance of a low-slope roof. The guide provides data and calculation procedures for estimating energy and cost savings. In most instances, the cooling cost savings associated with a change to a white roof surface (one with higher solar reflectance) exceed the heating cost penalty. If the difference between reduced cooling costs and increased heating costs is significant, it can affect the choice of membrane for a new roof or a re-roofed building. The guide helps the user estimate this energy cost difference and also describes how various factors influence potential energy savings and actual roof surface temperatures for different solar reflectance.

 

Parker, D., & Barkaszi, S. (1994). “Saving Energy with Reflective Roof Coatings”, Home Energy Journal, May-June, pp. 15-20.

 

This paper contains information of six case studies out of ten case studies that the Florida Solar Energy Center conducted in Florida during midsummer over a period of four years. The studies measured the effect of increasing the roof surface solar reflectance on air conditioning energy use and shows that reflective roofs can reduce space-cooling energy consumption and demand in Florida. The savings is about 10-40% that is around 440 to 1760 kWh per year for household electricity use or an annual saving of $35-$140 at current electricity rates (assuming 8 cents per kWh). The savings will vary depending upon the severity of the cooling season and roof insulations. The paper discusses the payback concern of reflective roofing which overall application would cost about $1 per ft² or approximately $2,200 for a typical home. With annual energy saving in Florida of $35-$140, the payback times are long, usually, lasting longer than the roof itself.

 

Parker, D. S., Cummings, J. B., Sherwin, J. R., Stedman, T. C., & McIlvaine, J. E. R. (1994). Measured Residential Cooling Energy Savings from Reflective Roof Coatings in Florida. ASHRAE Transactions, Vol. 100, Pt. 2, pp. 36-49.

 

This study presents experiments about the impact of reflective coating on air conditioning energy use that were applied to the roof of two residential buildings in Cocoa Beach, Florida, in the summer of 1992. Site 1 with approximately R-11 (RSI 1.9) ceiling insulation and Site 2 with a flat roof with no insulation. Reflective coatings were applied to the roofs of both residences in mid-summer. Analysis revealed substantial reductions in space-cooling energy use in both homes. Air-conditioning energy use was reduced by approximately 25% at Site 1. Utility coincident peak demand between 5 and 6 p.m. was reduced by 28%. Cooling energy savings at the uninsulated Site 2 home were approximately 43% and the coincident peak reduction was 38%.

 

Parker, D. S., Huang, Y. J., Konopacki, S. J., Gartland, L. M., Sherwin, J. R. & Gu, L. (1998). Measured and Simulated Performance of Reflective Roofing Systems in Residential Buildings. ASHRAE Transactions, Vol.104, Pt. 1B, pp. 963-975.

 

This paper contains information about a series of experiments in Florida residences that have measured the impact of increasing roof solar reflectance on space cooling. In tests on eleven homes with the roof colour changed in mid-summer, the average cooling energy use was reduced by 19%. Measurements and infrared thermography show that a significant part of the savings is due to interactions when the duct system is located in the attic space. An improved residential attic and duct simulation model, taking these experimental results into account, has been implemented in the DOE-2.1E building energy simulation program. The model was then used to estimate the impact of reflective roofing in fourteen climatic locations around the United States.

 

Parker, D. S., Sherwin, J. R., & Sonne, J. K. (1998). Measured Performance of a Reflective Roofing System in a Florida Commercial Building. ASHRAE Transactions, Vol.104, Pt. 1B, pp. 789-794.

 

The paper reports on the first results from tests on a reflective roofing system on a commercial building in Florida. The building is an elementary school with a sloped, modified bitumen roof. Air conditioning power was measured in a base configuration prior to the roofing system being changed to a white colour. Roof, decking, and plenum air temperatures were strongly affected by the change to a white roof system. The school, which was monitored for a full year in both the pre- and post-condition, saw the measured annual chiller electric power reduced by 10%, or 13,000kWh/yr. Cooling-load reductions during the utility summer peak were substantially greater, more than 30% during the afternoon hours.

Petrie, T. W., Childs, P. W., &Christian, J. E. (1998). Radiation Control Coatings Installed on Rough-surfaced Built-up Roofs: Initial Test Results. ASHRAE Transactions, Vol. 95, Pt. 2, pp. 795-809.

This paper is a study on the solar reflectance and thermal performance of small samples of various radiation control coatings on smooth surfaces that have been tracked for several years on a roof test facility in East Tennessee. The focus is on white coatings because of their potential to weather, which causes the solar reflectance to decrease as the coatings age. An extension of the study included more small samples on smooth surfaces and entire rough-surfaced roofs at a federal facility in Florida. Two rough-surfaced, moderately well insulated, low solar reflectance built-up roofs (BURs) were spray-coated with a latex-based product including ceramic beads. Only a small patch was left uncoated on each BUR to gather data throughout the project on the performance with no coating for direct comparison to data from instrumented coated areas. The average power demand during occupied periods for the first month with the coating for the building with the thermally massive roof deck was 13% less than during the previous month without the coating. For the other building, with a lightweight roof deck but high internal loads, there were no clear average power savings due to the coating.

 

Petrie, T. W., Childs, P. W., & Christian, J. E. (1998). Radiation Control Coatings on Rough-surfaced Roofs at a Federal Facility: Two Summers of Monitoring Plus Roof and Whole Building Modeling. Proceedings of the ASHRAE/DOE Conference on Thermal Performance of the Exterior Envelopes of Buildings VII, Clearwater Beach, FL., pp. 353-371.

 

This paper updates and completes the presentation of data for this New Technology Demonstration Programme (NTDP) project. The paper discusses the effect of radiation control coatings on rough-surfaced, low-slope roofs at a federal facility in the Panhandle of Florida. Two gravel-topped, moderately well-insulated, low solar reflectance built-up roofs (BURs) were spray coated with a white, latex-based product with ceramic beads. One roof was significantly shaded and its building had high internal loads. The other had a thermally massive deck but its building had little internal load. Measurements show the history of coated and uncoated outside-surface temperatures and solar reflectance of the roof surfaces from July 1996, when the roofs were coated, through October 1997. Roof models based on one-dimensional transient conduction through the roofs are used to compare the heat fluxes through the roof deck for coated and uncoated roof surfaces. DOE-2.1E whole building annual energy use predictions specific to the buildings and their operating schedules show the effect of the coatings and other building features for the climatic conditions of the Florida Panhandle.

 

Rosenfeld, A. H., Akbari, H., Taha, H., & Bretz, S. (1992). Implementation of Light-Colored Surfaces: Profits for Utilities and Labels for Paints. Proceeding of the ACEEE 1992 Summer Study on Energy Efficiency in Buildings: Efficiency & Sustainability, Vol. 9, pp. 9.141-9.144.

 

This study discusses about the problem of summer urban heat islands that requires significant additional generating capacity and results in increased pollutant emissions and higher energy bills. Urban areas can be lightened through use of high-albedo materials for both building and urban surfaces. The paper estimates that heat island reduction savings of $1 billion could be realized through utility-sponsored demand-side management (DSM) programs that promote the whitening and greening of cities. Assuming these utilities are permitted to retain 10% of program savings, then they could earn about $100 million/year.

 
Jeff

8=!   8=)  :=)   8=)   ;=)   8=)   8=(   8=)   8=()   8=)   8=|   8=)   :=')   8=)   8=)   8=?

Jeff S. Haberl, Ph.D., P.E.............................jhaberl@xxxxxxxxxxxx
Associate Professor....................................Office Ph: 979-845-6507
Department of Architecture...........................Lab Ph: 979-845-6065
Energy Systems Laboratory...........................FAX: 979-862-2457
Texas A&M University..................................77843-3581
College Station, Texas, USA...........................URL: www-esl.tamu.edu

8=/   8=)  :=)   8=)  ;=)   8=)   8=()   8=)   :=)   8=)   8=!   8=)   8=?   8=)   8=)   8=0  

 

======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx