Unfortunately, the ARI data for performance at
partial loads is not useful in an hourly simulation program, precisely because
it makes an assumption about reduced condenser temperature at reduced
load. The assumptions in the ARI curve might be reasonable for a single
chiller in a given building and climate, and where you allow the condenser
temperature to drop with load and wetbulb. However, many plants have more
than one chiller, the cooling tower(s) may be controlled to a fixed
condenser temperature, and/or you might be running the chiller in Florida
vs. New Mexico, which have very different load/wetbulb
relationships.
It would be useful if ARI recognized these
issues, and developed a standard method for reporting chiller performance for
use in hourly simulation programs (the same problem also applies to packaged
rooftop equipment).
Note that "standard" ratings assume the evaporator
is operating at 44F leaving temperature and 2.4 gpm/ton, and the
condenser is operating at 85F entering and 3.0 gpm/ton. However a
centrifugal chiller is custom built to the engineer's specifications. A
chiller in a low-wetbulb climate may be configured to run with 75F entering
condenser water, and will surge if operated at 44F/85F. In other words,
many centrifigal chillers cannot operate at the "standard"
conditions!
The default curves in recent versions of 2.2 are
based on a manufacturer's proprietary data. They are an improvement
over the 2.1e curves, but do not necessarily represent all chillers and all
manufacturers.
DOE-2 uses three curves to model chiller
performance. The use of these curves is documented in the Topics
manual. More recent versions of 2.2 modify performance for off-rated
condenser flow. In addition, the PLR curve includes a second term
(PLR,dT) to model the condenser relief necessary to achieve savings with a
variable-speed drive.
=====================================================You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx |