[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[BLDG-SIM] Major disagreement on Chiller Performance Curves in DOE-2.1E and DOE-2.2
Title: Message
John,
I think the answer to your question has two parts:
1. DOE
uses two curves for modifying the full load EIR (1/COP) of a
constant speed chiller. The first adjusts for part load and the
second for temperature.
I use a curve with fixed CHWT and CWT at various part
load conditions (at design conditions not ARI rated
conditions) for the EIR f(PLR) curve (the one you're asking about) and
create a second curve based on various combinations of CHWT, CWT at full
load for the EIR f(LCHWT, ECWT) curve. The assumption, I think, is
that the PLR curve reamins relatively uniform as the water temperatures change
so once you have the shape of the PLR curve you can account for
temperature differences with a second curve.
2. The
above methodology works fine for constant speed chillers but needs to be
modified for variable speed chillers. Rather than using EIR F(PLR) you
need to use EIR f(PLR,dT). This curve now accounts for the change
in the difference of the water temperature across the chiller. See
Volume 6 of the DOE 2.2 v41 reference manual available at www.DOE2.com, there is a section on chiller
performance that explains this much better than I could do. DOE
2.2 v41 incorporates this change and has default curves for
both.
It
sounds like you both may be correct depending on the type of chiller you want to
model.
Mike
Tillou, PE
etc
Group, Inc
413-664-9070
-----Original Message-----
From:
postman@xxxxxxxx [mailto:postman@xxxxxxxx] On Behalf Of Aulbach,
John
Sent: Wednesday, October 15, 2003 2:23 PM
To:
BLDG-SIM@xxxxxxxx
Subject: [BLDG-SIM] Major disagreement on Chiller
Performance Curves in DOE-2.1E and DOE-2.2
I am having a "friendly" disagreement with a colleague on what
chiller curves to ask for from a manufacturer to input into DOE-2 (could be
either 2.1E or 2.2). We both agree that the infamous ARI point for a 100% load
should be input. But the curves are where we disagree.
Is the Default DOE-2 curve for % Power versus % Tons the ARI
curve with the allowable reduction in condenser water temperature, or is it
based on the FIXED 85°F entering condenser water and FIXED 44°F leaving
chilled water ALL the way down the curve?
Therefore, when I am given a chiller with a variable speed
drive installed, what parameters should I ask for in such a Power/Tons to be
FIXED ???
John R. Aulbach, PE, CEM
Project
Engineer
Sempra Energy Solutions
555 West Fifth Street
Mail Location 27F3
Los Angeles, CA 90013
Tel: (213)
244-8551 Cell (213) 219-4875
"Sempra Energy Solutions is not the same company as SDG&E/
SoCalGas, the Utilities. Sempra Energy Solutions is not regulated by the
California Public Utilities Commission, and you do not have to buy Sempra
Energy Solutions products or services to continue to receive quality regulated
service from the Utilities."
==================
You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx
=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx