[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[BLDG-SIM] DOE2.1E PTAC cooling coil module
Hi,
It appears as though the PTAC cooling coil routine in DOE2.1E is overestimating latent load on the coil.
As shown by the lines of DOE2.1E code listed below, the sensible load is calculated via an averaged supply air temperature (TS), which is derived from the zone load and temperature. Since the PTAC cooling coil runs either fully on or fully off, the value of TS in a part-load condition becomes a time weighted average between the temperature of the air off the cooling coil in the ON mode and the mixed air temperature. I believe this is all correct.
IF(PO .GT. 0.0) PTAC 150
1TS = TAVE - <QNOW>/(CONS(1)*<CFMAX>*LSR(1)) PTAC 151
.
.
.
C CALC UNIT COOLING LOAD. PTAC 209
7 CONTINUE PTAC 210
ZQC = AMAX1(0., (TM-TS)*CONS(1)*FC) PTAC 211
C THEN ANY MOISTURE REMOVAL INCREASES THE LOAD PTAC 212
ZQC = ZQC + AMAX1(0.,WM-WCOIL)*CONS(2)*FC PTAC 213
The latent load, however, is calculated from the ON mode leaving coil moisture value with no adjustment for the off-time in a given hour. I would expect that an adjustement such as the following line would be needed to only allow latent load for the time that the coil is on.
IF (DTMC.GT.0) ONTIME = (TM-TS)/(TM-TC)
Am I missing something here? I think I can fix the problem with a function, but I want to make sure I'm not mistaken that it is a problem.
Thanks,
Doug Maddox
The Weidt Group
dougm@xxxxxxxx