[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[BLDG-SIM] Static Pressure Reset of Supply Air
Mike,
I suggest looking at a recently published guideline available at the
California Energy Commission's website. The Advanced VAV System Design Guide
has quite a bit of information about supply pressure reset and even includes
some DOE2 fan curves developed to approximate the performance (see page
198). Note that the file size is about 4MB.
http://www.energy.ca.gov/reports/2003-11-17_500-03-082_A-11.PDF
Erik Kolderup
Architectural Energy Corporation
(formerly Eley Associates)
-----Original Message-----
Although our company works with VisualDOE, this question is applicable to
DOE-2.1 in general.
If I model a VAV system with supply air temperature reset based on warmest
zone or an outside air schedule, this will at times cause the originally
satisfied VAV boxes to open further and increase fan power.
Is it possible to model static pressure reset where the static setpoint is
reduced if all boxes are satisfied? I'd be curious to see how the cost of
fan energy and heating/cooling energy varies between the two control
strategies.
Thanks.
Mike Busman, C.E.M.
Senior Project Engineer
NORESCO, LLC
17671 Cowan, Suite 206
Irvine, CA 92614
tel. 949-253-3533, ext. 303
fax 949-253-2049
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx