The last TES I did was for a military base. I think the base energy manager
must have gone to a seminar and picked up the buzz word, because he wanted
TES. We tried to talk them out of it and just go with a new water-cooled
central chilled water plant to replace about 10 rotten air-cooled chillers.
We explained that TES requires the right combination of factors, including
high demand charge, high peak hour time of use kWh charge, low off peak TOU
kWh charge, and quite often a utility company or state rebate for demand
reduction programs to make the project economically viable. Well they
wanted their TES and wanted ice storage versus chilled water storage.
Fortunately, as this was a super ESPC project, the customer was able to kick
in a few $$ to cover the incremental cost of the ice tanks and associated
equipment and the rest of the project funded as an energy savings perforance
contract. Fortunate, because the electric rates were not conducive to TES.
Perhaps, the customer saw other value or intangible benefits from the TES.
As expected, between circulating glycol through the chillers and taking the
performance hit of recharging the ice tanks with an evaporator temperature
in the 22 deg.F - 26 deg.F range,kWh consumption during ice charging period
went up. In the end, though, the difference in kW/ton between the old
air-cooled recips with corroded condensers and the new electric screw
chillers measurement and verification (and the few $ of buydown on the TES
portion) were sufficient and made for a successful project. One final note
of interest. We ran an analysis with and without the TES and as I recall,
the TES only contributed a couple of $thousand/year in savings with about
98% of the electric savings coming from the improved kW/ton of the electric
cooling.
So, don't believe all the buzz words, get the correct rate data and chiller
part-load data..........and the customer is always right.
Mike Busman
Senior Project Engineer
NORESCO, LLC
-----Original Message-----
From: Chris Jones [mailto:cj@xxxxxxxxx]
Sent: Friday, November 26, 2004 10:23 AM
To: BLDG-SIM@xxxxxxxx
Subject: [BLDG-SIM] Simulation on Thermal Energy Storage using DOE2.2
We did an analysis of an existing building with a large heat/cool storage
system. The Owners were very surprised to find out that the building was
not energy efficient - it just saved on demand charges. The pumping of
fluid in and out of the tanks, through heat exchangers occurred 24 hours a
day significantly increasing the kWh beyond that of a conventional hydronic
heat/cool building.
At 01:26 11/26/2004, you wrote:
>Dear Martin,
>I think the findings may be correct.
>First, for a TES system the leaving chilled water temperature usually will
>be lower, so the COP will be deduced, but as the outside temperature is
>lower, it does not deduced alot.
>Second, if the TES system using brine water, i think the efficiency will
>reduce more.
>As our experience in some project in Hong Kong and Mainland, TES system
>can only reduce electricity cost due to tariff rate rather than
consumption.
>I hope these comment would help.
>
>Regards,
>Ernest Tsang
>Meinhardt (M&E) Ltd
>
>
>Martin Yip <yipch@xxxxxxxxxxx> wrote:
>Dear Bldg-sim Subscribers,<?xml:namespace prefix = o ns =
>"urn:schemas-microsoft-com:office:office" />
>
>I recently simulated an air cooled chiller plant with cold water tank
>thermal energy storage using DOE 2.2. I originally expected some energy
>saving due to improve chiller COP at night charging the storage when
>compare it with a system without storage. However, the results showed an
>energy penalty of a few percentages even though hourly data actually
>showed COP improvement during charging. I have already set the loss
>coefficient to zero for the TES. I should be most grateful if anyone can
>comment on this issue and provide some suggestion.
>
>Thanks
>
>Martin YIP
>Engineer
>EMSD, HKSAR
>
>
>
>
>=====================================================You received this
>e-mail because you are subscribed
>
>to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe
>
>from this mailing list send a blank message to
>
>BLDG-SIM-UNSUBSCRIBE@xxxxxxxx
>ɹL¡B¤@©ç¨â´²¡B©_¬¥§õºû´µ¦^«H...
>¥þ´ä³Ì¤j¤â¾÷¤U¸ü¤¤¤ß
><http://us.rd.yahoo.com/evt=22281/*http://hk.yahoo.com/mail_tagline/?http:/
/mobile.yahoo.com.hk/>http://mobile.yahoo.com.hk/
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Chris Jones
EnerSys Analytics Inc.
14 Oneida Avenue
Toronto, ON M5J-2E3
Tel. 416 203-7465
Fax. 416 946-1005
=====================================================You received this
e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx