[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[bldg-sim] Lighting Energy



At 04:03 PM 2/18/2005 Friday, Varkie Thomas wrote:
Who should I contact at IECC for interpretation of the code? In the meantime I have some questions (pardon my ignorance) regarding lighting.
 
IECC-2000, page 114, table 805.4.2 (also in the Chicago Building Code) shows the following lighting power densities for office building:
 
Entire
Building:                                     1.3 W/ft2
Tenant Area or Portion of Building:      1.5 W/ft2
 
There is a Note ?b? associated with office (and also classrooms/lecture halls) which states:
 
?Where lighting equipment is specified to be installed to meet requirements of visual display terminals as the primary viewing task, the smaller of the actual wattage of the lighting equipment or 0.35 W/ft2 times area of space that the lighting equipment is in shall be added to the interior lighting power determined in accordance with this item?
 
I assume that the entire building area is the gross area which includes the core (elevator & duct shaft plan sections) and underground parking. The net area is about 15% less than the gross area and this would be the tenant area. 1.3 W/ft2 * 1.15 = 1.5 W/ft2
 
Is the ?lighting equipment? task lighting only, or does it include other equipment such as projectors?

It usually includes task lighting only on the assumption that it would be used on the task lighting schedule in sync with general lighting.  Projectors are used intermittently and can usually be ignored.  Even if they are used very often and considered, they probably fit better into the equipment loads.


Are computer monitors (visual display terminals) a ?lighting equipment? since it also generates light?
 

The intent of the lighting load is to simulate energy usage and heat gain from the lights.  The computer monitors do not really fit that category (unless the computer monitor is being treated as a source of light instead of say an overhead lamp, which does not seem very likely).  Computer monitors again would be more appropriately accounted for in equipment.

What is ?the smaller of the actual wattage of the lighting equipment or 0.35 W/ft2 times area of space that the lighting equipment is in shall be added to the interior lighting power?? Given a tenant space of 100 ft2 that has 1.0 W/ft2 general lighting and a 100 watt task light, what is the area lighting of the space for code compliance?

If the task lighting is already designed, then that actual wattage is the design case lighting.  In that case, if the design lighting is higher than 0.35 W/ft2, the code lighting is 0.35 W/ft2; if the design lighting is less than 0.35 W/ft2, then the code case lighting is coded same as the design lighting. In other words, you do not get credit for reducing task lighting below 0.35 W/ft2, but you do get penalized for going over.

If the task lighting is not designed yet, both design case and code case can assume 0.35 W/ft2 if it is definite that there will be some, as yet undetermined, task lighting in that area.
If there is going to be no task lighting in that area, both the design case and the code case should not have the task lighting load included.

Is there a lighting program or Excel spreadsheet program that will calculate the W/ft2 at the ceiling given the illuminance required at the task level, the type of lighting fixture or luminaire, and the ceiling height? I think manufacturers should provide this calculator for their luminaires.
 
How would you show energy savings for occupancy based lighting controls? In 10CFR435 Table 514.1 ?Power Adjustment Factor (PAF)?, the PAF for Occupancy Sensor is 0.3. When using energy analysis programs, can we reduce the lighting schedule fractions by 30% for the proposed design compared to the prototype or base design?

For the occupied periods only, the lighting schedule can be reduced by a fraction.  It is as exceptional method under code.

Increasing the percent glass of the envelope and increasing the ceiling height also reduces lighting usage because of increased daylighting. Daylight can now reach deeper into the interior. How would you show this energy savings using computer programs? Can the perimeter zone depth be increased to say 30 feet? The DOE2.1E program lets you locate two light sensors in the perimeter zones but the codes do not specify where in the zone. They could both be located 5 feet from the window as representing the entire perimeter zone depth.

ASHRAE Std User's manual defines the perimeter zone as 15 feet deep.  The sensor should be located well inside this zone, that is 10' inside, or at the very least, halfway inside at 7.5' to get a fair idea of energy savings from daylight for the entire zone.
LEED does give credit for 'daylight glazing' from high windows.. the calculation is clearly shown in the LEED manual.

Sincerely,
Smita

Varkie Thomas
 



======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx