[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[BLDG-SIM] eQUEST Condensing Boiler Curve



Title: eQUEST Condensing Boiler Curve

Using eQUEST v.3.6, I've taken a stab at creating a performance curve for an Aerco KC1000 condensing boiler. I've defined BOILER:HIR-FT = "Aerco-KC1000-HIR-fEWT&LWT" as shown below. This boiler is being used for a water source heat pump condenser water loop with a CT/HX & two condensing boilers, piped in a primary loop configuration.

"Aerco-KC1000-HIR-fEWT&LWT" = CURVE-FIT      
   TYPE             = BI-QUADRATIC-T
   INPUT-TYPE       = DATA
   INDEPENDENT-1    = ( 180, 180, 180, 80, 80, 80, 100, 100, 100, 120, 120,
         120, 140, 140, 140, 160, 160, 160 )
   INDEPENDENT-2    = ( 180, 90, 135, 90, 135, 180, 90, 135, 180, 90, 135,
         180, 90, 135, 180, 90, 135, 180 )
   DEPENDENT        = ( 1, 1.023, 1.019, 1.151, 1.077, 1.065, 1.102, 1.047,
         1.038, 1.053, 1.026, 1.017, 1.033, 1.017, 1.012, 1.023, 1.017,
         1.007 )
   ..

Question: Is this a proper curve for this equipment? Any comments and critiques would be much appreciated. Part of my difficulty is that HIR-FT is a Bi-Quadratic-T or Bi-Linear-T curve that needs two temperatures (EWT & LWT) to define the HIR ratio modifier. When looking at the curves, it's stated as thermal efficiency vs. EWT (return water temperature) on several different curves based on fire rate of the boiler. Basically, I assumed a LWT based on firing rate (90F=25%, 135F=75% & 180F=100%). I'm not sure if this is reasonable or not. Per the manual, the DEPENDENT variable is the ratio of the actual efficiency (based on the curves) / rated efficiency (at full fire, full load). INDEPENDENT-1 = EWT, INDEPENDENT-2 = LWT.

The link to the data sheet is here:
http://www.aerco.com/cgi-bin/docsserv.cgi?idDocument=344

Mark Nieman, PE, CEM
Sr. Energy Engineer
McKinstry Essention
Direct: (206) 832-8152
Cell: (206) 510-4760
FAX: (206) 832-8552
http://www.mckinstry.com
"For The Life Of Your Building"


=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx