Varkie, what we typically do is calculate
the projected temperature profiles using the ESHG method, then insert the
return temperature from the ESHG calc as the space operating temperature. This
way the underfloor supply CFM is only for the load it ‘sees’. Look at the
system pressure drops carefully and amend the fan pressure accordingly. Make
sure the systems have perimeter heating. Depending upon your location you are
right in checking the AHU to see if it dehumidifies the supply and doesn’t simply
provide air at 63F. Another way we check this is to run the same model but this
time with 55F and the same delta T as the underfloor model, checking the latent
loads between these models will give an indication of the dehumidification been
carried in the model. Good luck. Peter Simmonds Ph.D. Associate
From:
bldg-sim@xxxxxxxx [mailto:bldg-sim@xxxxxxxx] On
Behalf Of Varkie Thomas Are there any examples of modeling UFAD with DOE2.1E
(or EQUEST). This is a commercial project with electric heating in
climate zone 3A. The baseline System No. is 8 - VAV w/PFP
Boxes). The proposed is also PIU (DOE2). The perimeter zones up to
3 ft are served from the ceiling. The remaining interior zones have UFAD. The CHW
coil leaving temp of the primary air is 48F. The UFAD supply temp is 65
F. The ceiling return air temp is 78. The System MIN-SUPPLY-T = 65
and COOL-SET-T = 48. ZONE-FAN-RATIO = 1.74 ?? 80%
glass. The Baseline primary air is 53F and ceiling supply is
55F. The ceiling return air temp is 76. System MIN-SUPPLY-T = 55
and COOL-SET-T = 53. ZONE-FAN-RATIO = 1.1. 40% glass. Is all this correct? Increasing the ZFR
increases the Fan energy. Increasing the MIN-SUPPLY-T from 55F to 65F
increased the System Supply Air and Fan energy considerably. For UFAD is it acceptable to assume the following
space volume temps? $ Baseline Summer & Winter Space Volume Temp = 75 $ $ UFAD: 75F from 0' to 7' 85F from 7.1' to 10' Avg Summer Space Temp
= 78F $ $ UFAD: 75F from 0'
to 7' 65F from 7.1' to 10' Avg Winter Space Temp = 72F $ STD62.1-2004
Table 6-2 ‘Zone Air Distribution Effectiveness
(Ez)’ shows Ez = 1.0 for Ceiling Supply of Cool Air Ez = 1.2 for Floor Supply of
Cool Air and Ceiling Return. How would you apply
this in DOE2.1E for Under-floor Air Distribution? How is occupancy based
lighting modeled? Based on 10CFR435 Table 401.3.3. Lighting
Schedule = Max Design Lighting * Base Lighting Schedule * 0.7 ? How is occupancy based
ventilation modeled? Percent Outdoor Air for Hour = Maximum Design Percent
Outdoor Air * Occupancy Schedule Fraction. Apply this schedule in MIN-AIR-SCH
? V.C. Thomas =====================================================You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx ================== You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx |