[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[BLDG-SIM] New Calculation method for Baseline Fan Energyin Addendum R



LEED has approved the use of addenda to A90.1-2004 so Addendum 'ac' can be applied. The change to the Appendix G fan power formula was not included in an addendum because it occurred while 90.1 was still considered 'informative,' not 'normative,' as the currently proposed Addendum 'r' to A90.1-2007 is proposing to change. I believe the change to the fan power formula, however, was approved by LEED in a CIR, so you should be able to apply the new formula and pressure credits for the Appendix G PRM.
Bill
 
Bill Talbert, PE, LEED® AP
Mechanical Systems
Phone: (608) 441-6677
E-mail: btalbert@xxxxxxxxxx

Affiliated Engineers Inc.
5802 Research Park Blvd.
Madison, WI. 53719
Tel. (608) 238-2616
Fax. (608) 238-2614

>>> "Baker, Kristopher" <kbaker@xxxxxxxxx> 10/25/2007 10:47 AM >>>
Any ideas if we can apply the new methodology, indicated in either
Addenda ac for the 2004 version or addenda r for the 2007 version, to
the Appendix G Performance Rating Method?

KB
Kristopher S. Baker, PE
LEED(r) Accredited Professional
Associate
Senior Sustainability Specialist - Sustainable Design &
High Performance Building Technology
Syska Hennessy Group, Inc.

Tel: 703.629.8028
Direct Fax: 866.885.5621
Email: kbaker@xxxxxxxxx
http://www.syska.com
P Please consider the environment before printing this e-mail
________________________________

This email and any files transmitted with it are the property of Syska
Hennessy Group and are intended solely for the use of the individual or
entity to which they are addressed. The information contained herein may
include trade secrets or privileged or otherwise confidential
information and unauthorized review, forwarding, printing, distributing,
or using such information is strictly prohibited and may be unlawful. If
you received this message in error, or have reason to believe you are
not authorized to receive it, please promptly delete this message and
notify the sender by e-mail.
________________________________


-----Original Message-----
From: BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] On Behalf Of Michael
Rosenberg
Sent: Wednesday, October 24, 2007 10:03 PM
To: BLDG-SIM@xxxxxxxx
Cc: sferguson@xxxxxxxxxxx
Subject: [BLDG-SIM] New Calculation method for Baseline Fan Energyin
Addendum R

Mike and Andrew,

That is Addendum R that Andrew is referring to. It is actually Addendum
R to 90.1, 2007. Even though 2007 has not been published yet, ASHRAE is
already up to Addendum R. As for the calculation, Andrew made a good
catch. It is a typo and should read   CFM x 0.00094 + A  and CFM x
0.0013 + A.

Mike


Michael Rosenberg
Oregon Department of Energy
625 Marion St. N.E.
Salem, OR 97301-3742
Phone : (503) 373-7809
Fax: (503) 373-7806

>>> "Michael Tillou" <michael.tillou@xxxxxxxxx> 10/24/2007 11:39:01 AM
>>>
I think you mean to be referencing ASHRAE 90.1-2004 addendum ac not
addendum
r which includes two new methods for calculating fan power limits.  The
first looks at total Motor HP which isn't very useful for energy
modeling
purposes and the second looks at fan brake-horsepower.  The fan
brake-horsepower equations are "(CFM x 0.00094) + A"  and "(CFM x
0.0013) +
A" for constant volume and variable volume systems respectively.  CFM is
the
design airflow rate and A is the brakehorse power adjustement for
various
pressure drop adjustments given in Table 6.5.3.1.1B.

Mike

Michael Tillou, PE, LEED
Tillou Engineering, LLC
Williamstown, MA 01267
P: 413-458-9870 C: 413-652-1087


  _____ 

From: BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] On Behalf Of Andrew
Craig
Sent: Wednesday, October 24, 2007 11:56 AM
To: BLDG-SIM@xxxxxxxx
Subject: [BLDG-SIM] New Calculation method for Baseline Fan Energy in
Addendum R





I was wondering if anyone out there can explain the new calculation
shown
for baseline fan brake horsepower in Table G3.1.2.9 of Addendum R to
ASHRAE
90.1-2004?  At first glance, the equation doesn't make sense because you
are
subtracting a relatively small number (0.0013+A) from a large number
(CFMs)
leaving you with a ridiculously large baseline fan motor brake
horsepower.
Am I just reading this wrong or is there a typo?  Isn't there an easier
way
out there to calculate baseline fan energy (please see version 1 of
Appendix
G for another confusing calculation)?

Andrew Craig, EIT, LEEDR AP | Mechanical Designer

INTERFACE ENGINEERING
708 SW Third Avenue | Suite 400 | Portland, OR 97204

direct: 503.382.2696
office: 503.382.2266
fax: 503.382.2262
email: Andrew_C@xxxxxxxxx
web: www.ieice.com

Consultants of Choice to the Built Environment for over 35 years
Kirkland, WA | Portland, OR | Sacramento, CA | Salem, OR | SanFrancisco,
CA





==================

You received this e-mail because you are subscribed

to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe

from this mailing list send a blank message to

BLDG-SIM-UNSUBSCRIBE@xxxxxxxx


======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx


==================
You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx


=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe