Jon, Bill, Sam, et. al.;

For LEED EA Cr1, and EPACT analyses, the method should be Appendix G Performance Rating, not Chapter 11 Energy Cost Budget. Appendix G  has  its own tables and sections, which lay out the "Baseline."

 

Comparing campus CHW costs with electric cost for DX seems to be what App G requires if you are modeling dorm rooms with fan coils, but this raises a host of problems with extra costs (CUP amortization and O&M) which may be included in CHW rate but not in the DX system's electric rate. But an ill-considered CIR re-iterated that's how it should be done. This method appears to conflict one of the prime directives of baseline and budget comparisons:

 

G2 SIMULATION GENERAL REQUIREMENTS

G2.1 Performance Calculations. The proposed building

performance and baseline building performance shall be calculated

using the following:

(a) the same simulation program,

(b) the same weather data, and

(c) the same energy rates.

 

I think there are proposals to allow accounting for just the energy costs embodied in the CHW, however the ones I've heard of would also require "modeling" a portion of the campus CUP and distribution system even though it is outside the scope of the project and associated CDs (which was a limiting prime directive of any code-centered building simulation). USGBC does already recognize that for cogen CUPs. (https://www.usgbc.org/ShowFile.aspx?DocumentID=1354 ). I bet the EA Cr1 reviewers are allowing modeling of campus CUP, under the "existing HVAC systems" clause, expanded in scope from the CIR that allowed modeling of a portion of a new high school and part of the associated chiller plant. The LEED ref guide for EA Cr1 vaguely refers to using the "existing HVAC system, such as a central plant on campus..." in a paragraph that is sandwiched between two other paras specifically about baseline definitions, so it appears to be discussing baseline model system definition. However, the referenced text in ASHRAE applies only to the proposed building model.

 

I think App G should return to the ECB methodology for building heat/cool source (CHW vs. CHW, steam vs. steam) in all cases, but LEED should have a separate (easier) EA Cr1 points scale for campus CUP-served buildings. Maybe combined with a separate "LEED for CUPs"!

 

Sorry if this isn't helpful.  I guess folks disagree about what a fair revision to this would be. If anyone wants to comment to ASHRAE on Appendix G, now is the time. Go to http://www.ashrae.org/technology/page/331#672 and download the 90.1-2007 Addendum R zip file under Oct 12-Nov 26 public review. This includes forms and instructions for suggesting specific changes. Below is the forward to the addendum:

 

FOREWORD

This addendum changes Informative Appendix G Performance Rating Method into a Normative Appendix. Additionally, some language has been modified to make the Appendix Enforceable.

Please note that the entire content of this Appendix is open for public comment as the entire Appendix is changing from Informative to Normative.

Note: In this addendum, changes to the current standard are indicated in the text by underlining (for additions) and strikethrough (for deletions) unless the instructions specifically mention some other means of indicating the changes. In addition, the remainder of the text is open for public comment.

 

Do we need a separate mailing list for baseline (LEED, ASHRAE, EPACT, IRS, GGHC, Labs21!) banter? Is this what building simulation has come to? This is what my lunch break has come to.

 

--

Fred W. Porter, B.S., LEED A.P.
Senior Engineer
Architectural Energy Corp., Boulder CO

 


  

From: Jon Evans [mailto:jevans@xxxxxxxxxxxxxx]
Sent: Thursday, October 18, 2007 3:03 PM
To: BLDG-SIM@xxxxxxxx
Subject: [BLDG-SIM] [Campus Chilled Water] eQUEST: Central Chiller for Baseline?

 

Sam and others,

 

I have a follow-up question related to your response on 9/25 to purchased chilled water and LEED modeling.

 

I have a baseline building using ASHRAE 90.1 System 1 (PTAC Units). The proposed building is using campus chilled water and fan coil units or water source heat pumps.  Do I use electric as the source for the PTAC cooling, or the campus chilled water? Using campus chilled water with PTAC units is not a realistic option, but it seems like 90.1/LEED requires this (Table 11.3.2A in 90.1-2004)- would USGBC consider this fuel switching?

 

Also, as a general survey, what are the going rates for campus chilled water and steam?  I have seen ~$0.70/therm chilled water (generated by absorption chillers) and $0.35/therm for steam for a college dormitory. I think these rates will vary by campus and end use.

 

Thanks for your guidance in advance.

 

-Jon


  

From: BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] On Behalf Of Sam Mason
Sent: Tuesday, September 25, 2007 8:31 AM
To: BLDG-SIM@xxxxxxxx
Subject: [BLDG-SIM] eQUEST: Central Chiller for Baseline?

 

Yoko,

In note 5 under Table 11.3.2A, 90.1-2004 says for systems using purchased chilled water, no chillers shall be modeled and CHW costs shall be determined using the adopting authority’s utility rates.  For both the baseline and proposed buildings, you would not include central chillers and instead use purchased chilled water.

 

Sam

 

--
Sam Mason
Atelier Ten
sam.mason@xxxxxxxxxxxxxx
 


  

From: BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] On Behalf Of Yoko Matsuyama
Sent: Monday, September 24, 2007 8:09 PM
To: BLDG-SIM@xxxxxxxx
Subject: [BLDG-SIM] eQUEST: Central Chiller for Baseline?

 

Hi, everyone,

 

I am modeling a building that is served chilled water from a central chiller, and the building doesn't have any individual chiller. 

I am wondering if  the baseline model (by ASHRAE 90.1-2004) should follow ASHRAE specified "type and number of chillers" (TABLE G3.1.3.7, ASHRAE 90.1-2004) depending on building conditioned floor area, or it should be modeled with a Central chiller as proposed/designed model. 

 

Thank you for your help

 

 

YM

Graduate Mechanical Engineer

 
 
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx
 
 
nt>
0pt'>BLDG-SIM-UNSUBSCRIBE@xxxxxxxxxx received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx

=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM@xxxxxxxx mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@xxxxxxxx