OK All,
Has anyone looked at this
lovely document, which is the Department of Energy's test procedure for
air conditioners and heat pumps to determine EER and SEER? To
this I turned to answer the burning question "what is the standard
external fan static pressure drop specified to calculate EER and
SEER?"
Seems to me after wading through the swamp
of equations in the back of the document that fan energy in EER and SEER
calculations is specified at a 0.05 inch external static pressure
drop.
So then I started digging around for data to support my
intuitive feeling that fan energy is going to be something like 1/10th that
of compressor energy on small heat pumps.
In the process I ran across this nifty DOE/ORNL Heat Pump Design
Model. Now we're cooking... see this
post for a 3D plot of parametric runs (did I say 'nifty'?),
varying supply airflow and static pressure, from 600 to 4200 and 0.05 to 0.65
respectively.
I'm standing by my assertion that supply fan energy does
not need to be subtracted from heat pump EER as SEER and the new number
recalculated -- playing those kinds of games can lead to an exercise in
futility.
Best regards,
Brandon Nichols,
PE, LEED®
AP
Mechanical
HARGIS ENGINEERS
600 Stewart Street Suite 1000 Seattle, WA 98101 www.hargis.biz d | 206.436.0400 c | 206.228.8707 o | 206.448.3376 f | 206.448.4450 From: Fred Porter [mailto:fporter@xxxxxxxxxxxxxx] Sent: Friday, October 12, 2007 5:22 PM To: BLDG-SIM; Brandon Nichols Subject: RE: [BLDG-SIM] Heat Pump COP G3.1.2.1 Equipment Efficiencies. All HVAC equipment in the baseline
building design shall be modeled at the
minimum efficiency levels, both part load and full load, in
accordance with Section 6.4. Where efficiency ratings, such as
EER and COP, include fan energy, the descriptor shall be
broken down into its components so that supply fan energy can
be modeled separately. G3.1.2.4 Fan System Operation.
Supply and return
fans shall operate continuously whenever spaces are occupied
and shall be cycled to meet heating and cooling loads during
unoccupied hours. If the supply fan is modeled as cycling and
fan energy is included in the energy-efficiency rating of
the equipment, fan energy shall not be modeled
explicitly. -- Fred
From: Brandon
Nichols [mailto:BrandonN@xxxxxxxxxx] Good
point Fred, for larger unitary packages and for dialing-in energy savings
rebate studies. I did say 'arguably', and yours is an insightful
observation. Scanned all 90.1-2004 but didn't see the reference you
alluded to -- if you can be more specific please
advise. Given the small
heatpumps my firm is accustomed to installing, coupled with the fuzzy level of
design at which we're doing our preliminary energy studies, the simplification
of discounting fan operation when compressors aren't running I think is well
within the error bars of the overall study. Which doesn't
provide any comfort from the realization that this business gives one plenty of
cause to ask where picking the theoretical flyspecs out of manufacturer's
published pepper has crossed a threshold of mind-numbingly diminished
returns! Regards
Brandon Nichols,
PE, LEED® AP Mechanical HARGIS
ENGINEERS www.hargis.biz d
| 206.436.0400
c |
206.228.8707 o
| 206.448.3376
f |
206.448.4450 From:
BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] On Behalf Of Fred Porter The method cited below
only gives correct results if the heat pump fan operates intermittently on a
call for heat/cool, and if the fan as installed runs at its ARI-tested power.
Otherwise this method greatly under-estimates fan energy, at least for constant
speed fans. This is mentioned specifically for App G/ECB models either in the
Standard itself or in the UM. -- Fred
From: Brandon
Nichols [mailto:BrandonN@xxxxxxxxxx] Good point, John -- but there may
be an arguably easier way to not double-count fan energy...following is a
reprint from the DOE2 documentation: COOLING-EIR
The Electric Input Ratio (EIR), or
1/(Coefficient of Performance), for the cooling unit at ARI rated conditions.
The program defines EIR to be the ratio of the electric energy input to
the rated capacity, when both the energy input and rated capacity are expressed
in the same units. This EIR is at ARI rated conditions, i.e., without correction
for different temperature or part load. Note: If you include fan electric
energy consumption in your value of COOLING-EIR, then you should set SUPPLY-KW/FLOW to zero (and SUPPLY-STATIC, SUPPLY-EFF and
SUPPLY-DELTA-T should be omitted). Otherwise, the supply fan electrical energy
will be double counted. For commercial systems the default value
of COOLING-EIR includes compressor and outdoor fan energy, but not indoor fan
energy. HEATING-EIR
Electric Input Ratio, or 1/(heating Coefficient of
Performance), for the heat pump. This EIR is at ARI rated conditions, i.e.,
without corrections for temperature or part load. The program-calculated HEATING-EIR
does not include fan power and heat. This keyword is appropriate only to HP,
RESYS, and PTAC systems. Mysteriously, the HEATING-EIR documentation
makes no mention of the fan energy double counting issue. But if you're
consistent and use 3.41 divided by the manufacturers published EER for the
cooling EIR, the inverse of the published COP for the heating EIR,
and zero-out the supply fan energy as described in the
documentaion ... then Bob's your uncle, right?
FWIW, that's the way we do
it... Brandon Nichols,
PE, LEED® AP
Mechanical
HARGIS
ENGINEERS www.hargis.biz
d
| 206.436.0400
c | 206.228.8707
o
| 206.448.3376
f |
206.448.4450
From:
BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] On Behalf Of Fred Porter Yes and no. The energy is "removed," but
the COP improves because the fan heat had a COP of 1.0, and is included in the
rated gross kW in and Btuh out. I think the T24 ACM may have a "method" or
formula.
From:
Aulbach, John Folks:
In eQuest, the Energy
Input Ratio (EIR) can be derived from EER or COP given for a unit or from a
Standard. To correctly model such a unit, one must subtract the fan energy for
the unit to obtain the EER (EIR) of the compressor only. This improves the input
from, say, a COP of 12.3 to 15. What about in the case
of the heat pump heating COP? Must one subtract out the fan energy here as well,
thus "worsening" the COP for the heating side? I cannot find anything
written on this subject. Thanks.
John R. Aulbach, PE, CEM
Project
Manager Nexant,
Inc. 100 North Barranca, Phone: 626-430-9054
Fax: 626-430-9060
email: jaulbach@xxxxxxxxxx
h@xxxxxxxxxxxxx received this e-mail because you are subscribedto the BLDG-SIM@xxxxxxxx mailing list. To unsubscribefrom this mailing list send a blank message toBLDG-SIM-UNSUBSCRIBE@xxxxxxxx======================================================You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx==================You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx=====================================================You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx |