| Yes and no. The energy is "removed," but the COP improves because the fan heat had a COP of 1.0, and is included in the rated gross kW in and Btuh out. I think the T24 ACM may have a "method" or formula. From: Aulbach, John Sent: Thu, 10/11/2007 3:25pm To: BLDG-SIM@xxxxxxxx Subject: [BLDG-SIM] Heat Pump COP Folks:
In eQuest, the Energy Input Ratio (EIR) can be derived from
EER or COP given for a unit or from a Standard. To correctly model such a unit,
one must subtract the fan energy for the unit to obtain the EER (EIR) of the
compressor only. This improves the input from, say, a COP of 12.3 to
15.
What about in the case of the heat pump heating COP? Must
one subtract out the fan energy here as well, thus "worsening" the COP for the
heating side?
I cannot find anything written on this
subject.
Thanks.
John R. Aulbach, PE, CEM
Project Manager
Nexant,
Inc.
100 North Barranca, Suite
820
West Covina, CA 91791 USA
Phone: 626-430-9054
Fax: 626-430-9060
email: jaulbach@xxxxxxxxxx
====================================================== You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx |