All; Or trying to in DOE-2.2. As Andrew points out; many or most of
these systems operate differently than the simple constant setpoint, or lack of
central heating coil, John describes. These are the DOE-2 defaults, and will
show little or no central heating unless OA is high and airflow is turn downed
considerably. But with the very common VAV AHU with gas furnace and electric
zone reheat, there is incentive to maximize the use of the furnace, for a
variety of reasons. Also the reference to preheating the OA is misleading with
respect to DOE-2 and most actual packaged VAV systems, as the preheat is
usually in the mixed air. Note that some VAV RTU furnaces can only
be used for warmup, they actually cannot turndown low enough to allow tempering
during normal occupied operation, and if the mixed air is cold, it will just be
sent down to the electric coils. For warmup periods, in typical practice
the supply air temp is set up to 85 or 95F for a while in the morning
until some control (return air, max or average of zones) signals that this
warmup period has been completed. Numerous variations of box damper control can
go along with this (all stay at minimum; open if below setpoint/close if
above). In general the reheat coils are kept off until the warmup period is
over. The warmup described in the DOE2 documentation merely indicates closing
the economizer, and turning the cooling coil off. As far as I can tell; DOE-2
cannot directly model the control of the zones and furnace now typical; and the
various workarounds we've tried to mimic it are brittle, error-prone, kludgy,
and/or neglect significant energy terms. They include:
If this typical practice can actually be
modeled as practiced, it would be nice to have detailed examples in some
documentation or somewhere on the DOE2.com website. If this common mode on a
common system can't be modeled as practiced, one of the utilities or states
that accept DOE2 simulation results for incentive calculations needs to
contract the DOE2 authors to implement more robust and realistic morning warmup
routines. Variations include using the central AHU furnace and supply air for
heating during all unoccupied periods. In some cases the simulation needs to
allow a scheduled variation in THERMOSTAT-TYPE from PROPORTIONAL to
REVERSE-ACTION during warmup or unoccupied central heating. Does anyone
know if E+ can model these sequences realistically? As far as the LEED/App G question; App G
meant for mixed/"hybrid" heat source systems/buildings to be compared
to all gas baselines (i.e. the electric coils would be replaced by HW coils
from a gas boiler). USGBC reviewers reinterpreted this in an EA Cr1 CIR to allow
the baseline to be a similar hybrid as the proposed. Oh yeah the gas consumption shown under
pumps/aux is the default pilot light. Set FURNACE-AUX to zero. -- Fred W. Porter, B.S., LEED A.P. From: Aulbach, John
[mailto:jaulbach@xxxxxxxxxx] Andrew: I don't know what your climatic area is,
but why should ANY heating show up at the central unit? A VAV w/reheat, in my
meager experience, is controlling the central cooling coil to 55 DegF and
adjusting reheat coils (and VAV airflows) from there. When winter shows up,
your cooling coil is REALLY backed off (or off) and the VAV still flies, with
heat added at the space (terminal) level. The only purpose you may have for a
central heating coil is to preheat outside air to, say, 40 DegF. Depending on
where your climate is, this may RARELY happen? Does this sound right, folks? From:
BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] On
Behalf Of Andrew Craig I have two questions that have come up recently...
Thanks for your input. Regards, INTERFACE ENGINEERING
direct: 503.382.2696 Consultants of Choice to the Built Environment
for over 35 years ==================You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxxSUBSCRIBE@xxxxxxxx blank message to bscribYou received this e-mail because you are subscribedto the BLDG-SIM@xxxxxxxx mailing list. To unsubscribefrom this mailing list send a blank message toBLDG-SIM-UNSUBSCRIBE@xxxxxxxx=====================================================You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx |