You are too generous Mike. I should heed my own advice on the documentation. Thanks for clarifying this.

I also thought and consulted a colleague (thanks Steve) on Taylor's chiller question:

For chillers, the second term in EIRf(PLR,dT) is important only for variable-speed centrifugal chillers. It is of negligible importance in other types of chillers. It is important in variable-speed, because the temperature differential is strongly correlated with the required speed of the impeller. If the dT is high enough, then the impeller may have to run at full speed even at low loads. The DOE-2 default curves are just that, defaults. Some folks find it necessary to create new curves to reflect their specific equipment. Cautions offered * verify the conditions (condenser/evaprator) for efficiencies at lower part loads are the same as for above 50%
* make sure the points are normalized around the rating condition

Sorry for my hasty response.

Kevin Madison


Michael Tillou wrote:
Actually Kevin didn't get the boiler hourly energy equation quite right. The actual equation is:
Hourly Boiler Energy = DesignCapacity * HIR * HIRf(plr)
The part of this that Kevin didn't explain is that the boiler HIRf(PLR) curve includes the PLR which explains why the curve is nearly linear. The value that the performance curve returns is actually
(HIRadj) * PLR
HIRadj = the multiplier that indicates how the full load HIR changes with respect to part load. If the boiler efficiency at a given part load goes down, HIRadj > 1. If the boiler efficiency goes up at a given part load HIRadj<1. HIRadj is really the ratio HIR-partload over HIR-fullload.
PLR = hourly load on the boiler / total capacity of the boiler
To create a curve that describes boiler HIR at various part loads you will need to divide the performance curve output at each part load point by the part load value and then multiply by the full load HIR. Taylor - You should double check your "custom" chiller curves I'm pretty sure from what you describe they are not correct. The Vol6 -New Features user manual does a good job describing how the chiller curves work. I suggest you review this. You can use the Excel function "LINEST" to create the necessary coefficients for a bi-quadratic curve from manufacturers chiller data. Typically you will need to request data for a specific chiller from the chiller rep. The hardest data to get is the chiller capacity data at various CHW/CW temperatures. Remember total chiller capacity is different than the rated 100% part load point, most chillers can provide 10-20% extra capacity. I have had good experience creating custom chiller curves for DOE2.2 and I think the default curves in eQuest are representative of the various chiller types. Obviously if you are evaluating a specific chiller you should try to create custom curves.
Mike
------------------------------------------------------------------------
*From:* BLDG-SIM@xxxxxxxx [mailto:BLDG-SIM@xxxxxxxx] *On Behalf Of *Kevin Madison
*Sent:* Thursday, October 04, 2007 9:46 PM
*To:* BLDG-SIM@xxxxxxxx
*Subject:* [BLDG-SIM] eQuest Default f(PLR) Skepticism

Perhaps it would help to clarify how DOE-2.2 (the simulation engine behind eQUEST) calculates hourly energy input for boilers and chillers.

For boilers, the hourly energy input is:
Hourly Energy = Cap(hour) * HIR * HIRf(plr)

So while the HIRf(plr) may increase as part load decreases, which is not uncommon for standard atmospheric boilers, the energy use will certainly decrease with plr because the required output of the boiler for the hour decreases.

For chillers, DOE-2 uses the following relationship to calculate the electricity input to the chiller each hour:

Caphour = Capacity * CAPf(t1,t2)
PLR = Load / Caphour
dT = t2 – t1
Elechour = Caphour * EIR * EIRf(t1,t2) * EIRf(PLR,dT) / 3413 Btu/kW

where

Caphour hourly capacity, Btuh (this is dependent on condenser and evaporator conditions for that hour)
Capacity rated capacity, Btuh
CAPf(t1,t2) correction to capacity for temperatures, curve CAP-FT
t1 leaving chilled-water temperature, °F
t2 condenser temperature, °F
PLR Part load ratio
Load Hourly load, Btuh
dT Temperature differential across chiller, °F
Elechour electric input to the chiller, kW
EIR rated electric input ratio
EIRf(t1,t2) correction to EIR for temperatures, curve EIR-FT
EIRf(PLR,dT) correction to EIR for part-load ratio and dT, curve EIR-FPLR

Again, the primary factor affecting chiller energy use is the cooling capacity needed for that hour. Just because you don't have access to the dual function information doesn't mean you shouldn't be accounting for it in the simulation. Chiller performance is dependent on all operating conditions including load, condenser conditions and evaporator conditions.

For a more complete discussion on these simulation concepts, refer to the DOE-2 documentation included with the eQUEST installation. Look in Dictionary:HVAC Components:Boiler:Boiler Energy Consumption and Dictionary:HVAC Components:Chiller:Chiller Energy Consumption.

Kevin Madison
Madison Engineering PS
Seattle WA
USA

Taylor Keep wrote:

eQuest models boiler and chiller plants with default part load curves that I think may be incorrect. As I understand it, the f(PLR) curves are used as a direct multiplier on the HIR for boilers and EIR for chillers, with full load (1.0 PLR) corresponding to a 1.0 multiplier. If this is true, the f(PLR) curve should increase at part load for atmospheric boilers (atmospheric boilers become somewhat less efficient at part load). The default atmospheric boiler curve decreases almost linearly down to zero! I am having a tough time wrapping my head around this.

On the chiller side, the default f(PLR) is a bi-quadratic function using both dT and PLR as variables, so it is f(PLR,dT). Since I never have this dual function information in my general chiller selections, I have been using a standard f(PLR) function quoted at a fixed dT from the manufacturer. The curve I get from a McQuay 400-ton chiller selection is quadratic, with decreasing EIR down to 50% load and increasing EIR below 50% load. I seriously doubt that the eQuest default corresponds with this entry because changing the function produces a huge change in performance.

Do any of you have any thoughts or suggestions about the accuracy of default f(PLR) curves? Should I scrap my "improved," real curves - they are drastically changing the model performance?!?!

Taylor


________________________________________________________
Taylor Keep
Mechanical, LEED® AP
_ _
Arup
901 Market Street Suite 260
San Francisco, CA 94103
tel: 415 946 0279
fax: 415 957 9096
taylor.keep@xxxxxxxx
_www.arup.com_ <file://www.arup.com>


____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
====================================================== You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx
======================================================
You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx ====================================================== You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx

======================================================
You received this e-mail because you are subscribed to the BLDG-SIM@xxxxxxxx mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE@xxxxxxxx